Daikin · Mini-split
F6 High pressure control in cooling
What the control is telling you
Outdoor coil temperature went above 60 C (140 F) in cooling and the unit cut frequency or stopped. It clears below 47 C (116.6 F).
Applies to: FTX30/36WVJU9 with RX30/36WMVJU9 or RK30/36WMVJU9
Likely causes
- Not enough clearance around outdoor unit
- Dirty outdoor coil
- Faulty outdoor fan motor
- Faulty stop valve
- Faulty expansion valve or coil
- Faulty outdoor coil thermistor
- Faulty outdoor PCB
Test and repair steps
- Turn off power at the disconnect before opening the unit or touching connectors. Check the installation space and airflow (check no. 17).
- Clean the outdoor coil.
- Check the outdoor fan (check no. 19).
- Check the discharge pressure (check no. 18).
- Check the expansion valve (check no. 12) and the coil thermistor (check no. 01).
Models that show this code
6 models in Daikin FTX-W
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Daikin FTX-W service manual SiUS042228E, Troubleshooting 4.18, p.94. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.