Daikin · Mini-split
F3 Discharge pipe temperature too high
What the control is telling you
Compressor stops when the discharge pipe goes above 120 C (248 F) and clears below 107 C (224.6 F). Repeats lead to shutdown. Resets after about 60 minutes of error-free running.
Applies to: FTX30/36WVJU9 with RX30/36WMVJU9 or RK30/36WMVJU9
Likely causes
- Faulty discharge, outdoor coil or outdoor air thermistor
- Faulty expansion valve or coil
- Refrigerant shortage
- Faulty four way valve
- Moisture in refrigerant
- Faulty stop valve
- Faulty outdoor PCB
Test and repair steps
- Turn off power at the disconnect before opening the unit or touching connectors. Check the thermistors (check no. 01).
- Check the expansion valve (check no. 12).
- Check the refrigerant line (check no. 14).
- Replace the outdoor main PCB if all of the above are good.
Models that show this code
6 models in Daikin FTX-W
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Daikin FTX-W service manual SiUS042228E, Troubleshooting 4.17, p.93. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.