F8 Compressor temperature abnormality shutdown

Critical severity Daikin FTX-W

What the control is telling you

Discharge pipe temperature reached 127.5 C (261.5 F) during forced cooling.

Applies to: FTX30/36WVJU9 with RX30/36WMVJU9 or RK30/36WMVJU9

Likely causes

  • Air got into the refrigerant system
  • Faulty discharge pipe thermistor

Test and repair steps

  1. Turn off power at the disconnect before opening the unit or touching connectors. Check the discharge pipe thermistor (check no. 01).
  2. If the thermistor is good, check the outdoor unit piping for deformation. The manual says to replace the outdoor unit as directed in the installation manual without letting air into the lines.
  3. If the thermistor is bad, replace it and the outdoor main PCB.

Models that show this code

6 models in Daikin FTX-W

FTX30WVJU9FTX36WVJU9RK30WMVJU9RK36WMVJU9RX30WMVJU9RX36WMVJU9

Other codes on the same units

  • E7 Outdoor DC fan lock
  • E8 Input overcurrent
  • F3 Discharge pipe temperature too high
  • F6 High pressure control in cooling
  • H0 Compressor current sensor abnormality
  • H6 Compressor position sensor abnormality (start failure)
  • H8 Current transformer (CT) abnormality
  • H9 Outdoor air thermistor fault

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Daikin FTX-W service manual SiUS042228E, Troubleshooting 4.19, p.96. Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.