Weil-McLain · Heat pump
F1 DC bus low voltage
What the control is telling you
The DC bus voltage on the inverter side is too low.
Applies to: ECO HP 41/48/55 MBH outdoor unit (ODU)
Likely causes
- Supply problem
- Main board fault
- Inverter board fault (bad IGBT)
- Rectifier bridge fault
Test and repair steps
- Check the supply voltage first.
- Inverter board can hold a charge power off and wait before touching it.
- If supply is good, check the board LED and the DC bus voltage. With the LED on, the manual says a 380 V reading usually points to the main board.
- If the LED is off, power down and check the IGBTs (diode test). Bad readings = replace the inverter board.
- If the IGBTs are good, check the rectifier bridge the same way.
- Tip F1 when the compressor starts usually means the main board. F1 when the fan starts may mean the inverter board.
Models that show this code
3 models in Weil-McLain ECO HP
Other codes on the same units
- E6 Outdoor air temperature sensor (T4) fault
- E7 Buffer tank temperature sensor (Tbt1) fault
- E8 Water flow fault
- E9 Compressor suction temperature sensor (Th) fault
- H0 Communication fault between indoor and outdoor unit
- H1 Communication fault between main board and inverter board (outdoor)
- H2 Refrigerant temperature sensor at plate HX outlet (heating) (T2) fault
- H3 Refrigerant temperature sensor at plate HX inlet (heating) (T2B) fault
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Weil-McLain ECO HP Split Air-to-Water Heat Pump ODU Product Manual 550-100-587/0824, sec. 11.8 Error codes, p.37. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.