HTP · Boiler
F05 Supply temperature high
What the control is telling you
Supply water temperature too high. At or above 210 F the message shows and clears when below 194 F. Above 230 F it becomes a lockout with FAULT light and LOCKOUT flashing. Pump on.
Applies to: EL-80, EL-110, EL-150, EL-220, EL-299, EL-399 (N/LP)
Likely causes
- Circulator not running or low flow
- Boiler circulator pumping the wrong way
- Supply thermistor fault
Test and repair steps
- Check circulator operation
- Confirm less than a 50 F rise from return to supply in the status menu
- Check the flow direction of the boiler circulator against the piping details
- Test the thermistor as for F02
Models that show this code
12 models in Elite EL
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Elite EL-80 N Installation Manual (LP-293), p. 70. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.