HTP · Boiler

F03 Return sensor failure

High severity Elite EL

What the control is telling you

Return temperature sensor has failed. Lockout, pump on. Control: FAULT light red steady and LOCKOUT shown on lower line; reset with RESET held over 1 second after repair.

Applies to: EL-80, EL-110, EL-150, EL-220, EL-299, EL-399 (N/LP)

Likely causes

  • Return sensor failed or wiring fault
  • Poor flow through the boiler

Test and repair steps

  1. Check circulator operation
  2. Confirm less than a 50 F rise from return to supply in the status menu
  3. Test the thermistor the same way as for F02

Models that show this code

12 models in Elite EL

EL-110 LPEL-110 NEL-150 LPEL-150 NEL-220 LPEL-220 NEL-299 LPEL-299 NEL-399 LPEL-399 NEL-80 LPEL-80 N

Other codes on the same units

  • E19 Line voltage frequency out of range
  • F00 Water high temperature (ECO)
  • F01 Flue temperature switch / low water
  • F02 Supply sensor failure
  • F04 Flue sensor failure
  • F05 Supply temperature high
  • F06 Return temperature high
  • F09 No flame on ignition

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Elite EL-80 N Installation Manual (LP-293), p. 70. Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.