HTP · Boiler
F02 Supply sensor failure
What the control is telling you
Supply (outlet) temperature sensor has failed. Lockout, pump on. Control: FAULT light red steady and LOCKOUT shown on lower line; reset with RESET held over 1 second after repair.
Applies to: EL-80, EL-110, EL-150, EL-220, EL-299, EL-399 (N/LP)
Likely causes
- Sensor wiring or connection fault
- Failed supply thermistor
- Control board not providing 5 V
Test and repair steps
- Check the connection to the thermistor on the outlet manifold
- Verify 5 VDC at the Molex connector; if missing, check the harness, and if the harness is good replace the control
- Check thermistor resistance against the resistance chart; replace the thermistor if needed
Models that show this code
12 models in Elite EL
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Elite EL-80 N Installation Manual (LP-293), p. 69. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.