F01 Flue temperature switch / low water
What the control is telling you
Flue temperature limit switch tripped or, if the optional UL353 LWCO is fitted, water level is low. Lockout with pump on. Control: FAULT light red steady and LOCKOUT shown on lower line; reset with RESET held over 1 second after repair.
Applies to: EL-80, EL-110, EL-150, EL-220, EL-299, EL-399 (N/LP)
Likely causes
- Low water level (UL353 LWCO installed)
- Flue obstructed or overheated
- Flue temperature switch failed
- Cracked target wall in the combustion chamber
Test and repair steps
- With an LWCO check for the red LED on its control box, correct the low water condition, press the LWCO reset (LED turns green) then reset the boiler at the display
- Check the flue for blockage or heat damage and repair
- Push the red reset button on the flue temperature switch (inside the rear access door); the switch must be below 90 F to reset
- Press RESET on the display, run the boiler and compare an external flue thermometer to the FLUE reading
- If the flue temperature is in spec and the switch trips again, replace the switch
- If the flue is hot, check combustion; inspect the target wall and replace if cracked
Models that show this code
12 models in Elite EL
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Elite EL-80 N Installation Manual (LP-293), p. 69. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.