HTP · Boiler
F09 No flame on ignition
What the control is telling you
Four ignition tries in one heat call all failed to establish flame. Lockout with pump on. Control: FAULT light red steady and LOCKOUT shown on lower line; reset with RESET held over 1 second after repair.
Applies to: EL-80, EL-110, EL-150, EL-220, EL-299, EL-399 (N/LP)
Likely causes
- No spark (spark electrode gap wrong or corroded)
- No gas or low gas pressure, air in gas line
- Flame rectifier probe dirty or faulty
- Blocked flue or condensate
Test and repair steps
- Watch the igniter through the sight window
- If no spark, check the spark electrode gap: 0.196 in. (5.0 mm +/- 1 mm)
- Clean corrosion from the spark electrode and the flame rectifier probe
- If there is spark but no flame, check the gas supply to the boiler
- If there is flame, check the flame sensor
- Check for flue blockage or condensate blockage
Models that show this code
12 models in Elite EL
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Elite EL-80 N Installation Manual (LP-293), p. 71. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.