HTP · Boiler
F13 Fan speed error
What the control is telling you
Fan speed is more than 30 percent off the commanded speed for over 10 seconds. Lockout with pump on. Control: FAULT light red steady and LOCKOUT shown on lower line; reset with RESET held over 1 second after repair.
Applies to: EL-80, EL-110, EL-150, EL-220, EL-299, EL-399 (N/LP)
Likely causes
- Fan wiring problem
- Failed combustion fan
- Overloaded external sensor terminals
- Failed control board
Test and repair steps
- Check the combustion fan wiring
- Measure DC volts from the red fan wire to ground with it connected: should be 24 to 40 V
- If below 24 V, check for excessive loads on the sensor terminals
- Unplug the 5-pin plug from the fan and re-measure: 24 to 40 V now means replace the fan
- Still below 24 V means replace the control board
Models that show this code
12 models in Elite EL
Other codes on the same units
- F06 Return temperature high
- F09 No flame on ignition
- F10 Flame loss
- F11 False flame signal
- F20 Condensate full
- F31 Program error
- CASCADE MASTER READY Cascade master ready
- CASCADE NO FOLLOWER Cascade - no follower
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Elite EL-80 N Installation Manual (LP-293), p. 72. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.