F13 Fan speed error

High severity Elite EL

What the control is telling you

Fan speed is more than 30 percent off the commanded speed for over 10 seconds. Lockout with pump on. Control: FAULT light red steady and LOCKOUT shown on lower line; reset with RESET held over 1 second after repair.

Applies to: EL-80, EL-110, EL-150, EL-220, EL-299, EL-399 (N/LP)

Likely causes

  • Fan wiring problem
  • Failed combustion fan
  • Overloaded external sensor terminals
  • Failed control board

Test and repair steps

  1. Check the combustion fan wiring
  2. Measure DC volts from the red fan wire to ground with it connected: should be 24 to 40 V
  3. If below 24 V, check for excessive loads on the sensor terminals
  4. Unplug the 5-pin plug from the fan and re-measure: 24 to 40 V now means replace the fan
  5. Still below 24 V means replace the control board

Models that show this code

12 models in Elite EL

EL-110 LPEL-110 NEL-150 LPEL-150 NEL-220 LPEL-220 NEL-299 LPEL-299 NEL-399 LPEL-399 NEL-80 LPEL-80 N

Other codes on the same units

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Elite EL-80 N Installation Manual (LP-293), p. 72. Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.