HTP · Boiler
F10 Flame loss
What the control is telling you
Flame was lost three times during one demand call. Lockout with pump on. Control: FAULT light red steady and LOCKOUT shown on lower line; reset with RESET held over 1 second after repair.
Applies to: EL-80, EL-110, EL-150, EL-220, EL-299, EL-399 (N/LP)
Likely causes
- Gas pressure dropping during operation
- Unstable flame
- Flame rectifier or spark probe dirty/worn
- Burner or burner door gaskets leaking
Test and repair steps
- Watch the gas pressure while the boiler runs
- Make sure the flame is stable
- See that the display goes from GAS VALVE ON to RUN within a few seconds of lighting
- Check the FLAME signal in the status menu: above 1.0 microamp while firing
- If under 1 microamp clean the flame rectifier and spark probe; if still low replace both
- Flame signal should be steady after 1 minute at about 5.0 to 9.0; if not, take the burner door apart and check the burner and gaskets
Models that show this code
12 models in Elite EL
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Elite EL-80 N Installation Manual (LP-293), p. 71, p. 72. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.