F8 Compressor temperature abnormality (discharge pipe)
What the control is telling you
Operation halts when the discharge pipe thermistor exceeds its limit. The detection threshold is 127.5°C / 261.5°F during forced cooling operation.
Applies to: FTXM-W/V outdoor unit, forced cooling
Likely causes
- Air intrusion into the refrigerant circuit
- Defective discharge pipe thermistor
Test and repair steps
- Turn off the power before connecting or disconnecting any connector.
- Check the discharge pipe thermistor (Check No. 01, p. 141).
- If the thermistor is faulty, replace both the discharge pipe thermistor and the outdoor unit PCB (main PCB).
- If the piping inside the outdoor unit is deformed, replace the outdoor unit.
- If air has entered the refrigerant piping, replace the unit as the installation manual directs, making sure no air enters the piping.
- If the thermistor checks normal and the fault remains, replace the outdoor unit.
Other codes on the same units
- C9 Room temperature sensor / humidity sensor abnormality (communication or malfunction)
- F6 High pressure control in cooling
- H0 Compressor system sensor abnormality
- H6 Position sensor abnormality (compressor start-up failure)
- H8 DC voltage/current sensor abnormality
- U0 Refrigerant shortage
- U2 Low-voltage or over-voltage detection
- CC Humidity sensor abnormality (communication or malfunction)
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: SiUS042113EA service manual, p. 131. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.