F6 High pressure control in cooling

Medium severity FTXM-W/V

What the control is telling you

High-pressure protection (operation halt or frequency drop) trips in cooling when the outdoor heat exchanger thermistor reads above the limit. Trip point is above 62°C / 144°F on 09/12 class and above 61°C / 142°F on 18/24 class. Clears when the temperature falls below 54°C / 129°F (09/12) or 52°C / 126°F (18/24).

Applies to: FTXM-W/V outdoor unit, cooling mode

Likely causes

  • Installation space too small
  • Dirty outdoor heat exchanger
  • Defective outdoor fan motor
  • Defective stop valve
  • Defective electronic expansion valve or coil
  • Defective outdoor heat exchanger thermistor
  • Defective outdoor unit PCB

Test and repair steps

  1. Turn off the power before connecting or disconnecting any connector.
  2. Check the installation space and location; correct it if airflow is restricted (Check No. 17, p. 148).
  3. Clean the outdoor heat exchanger.
  4. Check the outdoor fan (Check No. 19, p. 149); replace the fan motor or reconnect the connector/lead wires if faulty.
  5. Check the discharge pressure (Check No. 18, p. 149); replace the stop valve if faulty.
  6. Check the electronic expansion valve (Check No. 12, p. 143); replace the valve or coil if faulty.
  7. Check the outdoor heat exchanger thermistor (Check No. 01, p. 141); replace it if faulty.
  8. If all checks are normal but the fault remains, replace the outdoor unit PCB (main PCB).

Other codes on the same units

  • C9 Room temperature sensor / humidity sensor abnormality (communication or malfunction)
  • F8 Compressor temperature abnormality (discharge pipe)
  • H0 Compressor system sensor abnormality
  • H6 Position sensor abnormality (compressor start-up failure)
  • H8 DC voltage/current sensor abnormality
  • U0 Refrigerant shortage
  • U2 Low-voltage or over-voltage detection
  • CC Humidity sensor abnormality (communication or malfunction)

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: SiUS042113EA service manual, p. 129-130. Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.