Navien · Heat pump
F9 Line voltage too low or too high
What the control is telling you
The board saw supply voltage below 172 V or above 275 V. Normal supply is 208-230 V.
Applies to: NAZ17V36 (24K/36K), NAZ17V60 (48K/60K)
Likely causes
- Low or high supply voltage
- Loose line wires at the terminal block
- Outdoor PCB fault
Test and repair steps
- Measure line voltage at the unit terminal block with the unit running.
- Outside 172-275 V: fix the supply (breaker, wiring, utility) before going further.
- Power off at the disconnect and wait for the inverter board to discharge before touching wiring or the PCB.
- Tighten the incoming wires at the terminal block.
- Voltage is good and the code returns replace the outdoor PCB.
Models that show this code
2 models in Navien NAZ
Other codes on the same units
- F5 T5 compressor discharge sensor fault
- F6 T3 condenser coil sensor fault
- F7 T7 sensor fault
- F8 T7 sensor: condensate risk on the cooling plate
- H0 Communication fault between chips on the outdoor PCB
- H1 Lockout: outdoor coil too hot (P5 repeated)
- H2 Lockout: high pressure switch (P1 repeated)
- H3 Lockout: high pressure in heating (PD repeated)
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Navien NAZ Series Heat Pump Service Manual (V1.00), 4.2.3, p.31. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.