Navien · Heat pump
F7 T7 sensor fault
What the control is telling you
The outdoor board is reading the T7 sensor as open or shorted.
Applies to: NAZ17V36 (24K/36K), NAZ17V60 (48K/60K)
Likely causes
- Sensor plug loose or not seated on the outdoor PCB
- Open or shorted sensor
- Outdoor PCB not reading the input
Test and repair steps
- Power off at the disconnect and wait for the inverter board to discharge before touching wiring or the PCB.
- Pull the sensor plug and push it back on firmly.
- Unplug the sensor and measure its resistance. Compare it with the 7.3 R-T Table, p.72.
- Open, shorted or off-chart reading replace the sensor.
- Sensor reads right but the code comes back: replace the outdoor PCB.
Models that show this code
2 models in Navien NAZ
Other codes on the same units
- d0 Oil return cycle
- F4 T4 outdoor ambient sensor fault
- F5 T5 compressor discharge sensor fault
- F6 T3 condenser coil sensor fault
- F8 T7 sensor: condensate risk on the cooling plate
- F9 Line voltage too low or too high
- H0 Communication fault between chips on the outdoor PCB
- H1 Lockout: outdoor coil too hot (P5 repeated)
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Navien NAZ Series Heat Pump Service Manual (V1.00), 4.2.1, p.29. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.