Navien · Air conditioner
F9 Line voltage too low or too high
What the control is telling you
The board saw supply voltage below 172 V or above 275 V. Normal supply is 230 V.
Applies to: NAA17V36 (24K/36K), NAA17V60 (48K/60K)
Likely causes
- Low or high supply voltage
- Loose line wires at the terminal block
- Outdoor PCB fault
Test and repair steps
- Measure line voltage at the unit terminal block with the unit running.
- Outside 172-275 V: fix the supply (breaker, wiring, utility) before going further.
- Power off at the disconnect and wait for the inverter board to discharge before touching wiring or the PCB.
- Tighten the incoming wires at the terminal block.
- Voltage is good and the code returns replace the outdoor PCB.
Models that show this code
2 models in Navien NAA
Other codes on the same units
- F5 T5 compressor discharge sensor fault
- F6 T3 condenser coil sensor fault
- F7 T7 sensor fault
- F8 T7 sensor: condensate risk on the cooling plate
- H0 Communication fault between chips on the outdoor PCB
- H1 Lockout: outdoor coil too hot (P5 repeated)
- H2 Lockout: high pressure switch (P1 repeated)
- H3 High pressure abnormal (sensor over 3.6 MPa) - heating mode
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Navien NAA Series Air Conditioner Service Manual, 3.2.3, p.24. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.