F8 T7 sensor: condensate risk on the cooling plate
What the control is telling you
T4 and T7 read below 2°C (about 36°F), so the board sees a risk of sweating on the refrigerant-cooled plate over the drive module.
Applies to: NAA17V36 (24K/36K), NAA17V60 (48K/60K)
Likely causes
- T4 or T7 sensor out of range
- PCB reading the sensors wrong
Test and repair steps
- Power off at the disconnect and wait for the inverter board to discharge before touching wiring or the PCB.
- Measure T4 and T7 resistance and compare with the 6.3 R-T Table, p.61. Replace a bad sensor.
- Power up and check the T4 and T7 readings on the CHK display against a thermometer.
- Big difference with good sensors replace the outdoor PCB.
Models that show this code
2 models in Navien NAA
Other codes on the same units
- F4 T4 outdoor ambient sensor fault
- F5 T5 compressor discharge sensor fault
- F6 T3 condenser coil sensor fault
- F7 T7 sensor fault
- F9 Line voltage too low or too high
- H0 Communication fault between chips on the outdoor PCB
- H1 Lockout: outdoor coil too hot (P5 repeated)
- H2 Lockout: high pressure switch (P1 repeated)
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Navien NAA Series Air Conditioner Service Manual, 3.2.2, p.23. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.