Kinghome · Heat pump
F5 Outdoor discharge temperature sensor fault
What the control is telling you
The discharge sensor is open/shorted; the compressor stops after about 3 minutes of running.
Applies to: Kinghome KM09HT1DI, KM12HT1DI, KM18HT1DI, KM24HT1DI wall mini-splits; Kinghome KM09HF1DI to KM24HF1DI wall mini-splits (Gree GFH..DA/DB)
Likely causes
- Loose sensor plug or poor terminal contact
- Failed (open or shorted) sensor
- Fault in the board's sensing circuit
- Sensor not inserted fully in its pipe pocket
Test and repair steps
- Check that the discharge sensor plug is seated fully on the board header.
- Unplug the sensor and measure its resistance; compare it with the temperature/resistance chart in the manual appendix.
- Replace the sensor if the reading is open, shorted or far from the chart.
- If the sensor is good and the plug is secure, replace the control board.
- Confirm the sensor tip is seated in its tube.
Models that show this code
9 models in Kinghome KM HT1DI, Kinghome KM HF1DI
Other codes on the same units
- E9 Water overflow protection
- F0 Refrigerant recovery mode
- F1 Indoor room temperature sensor fault
- F2 Sensor fault (indoor coil or outdoor condenser)
- F3 Outdoor ambient temperature sensor fault
- F6 Frequency limit for overload / ODU tube sensor fault
- F9 Frequency reduced - high discharge temperature
- H3 Compressor overload protection
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Kinghome KM09-12-18-24HT1DI service manual, sec. 9.1 error code list; Kinghome KM09-24HF1DI service manual, sec. 11.1 error code list. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.