Kinghome · Heat pump

F2 Sensor fault (indoor coil or outdoor condenser)

Medium severity Kinghome KM HEDIKinghome KM HT1DIKinghome KM HF1DIKinghome Ultranixx EcoKinghome Ultranixx

What the control is telling you

On the wall units F2 is the indoor evaporator sensor open/shorted. On Ultranixx units F2 is the outdoor condenser temperature sensor.

Applies to: Kinghome KM09HEDI, KM12HEDI, KM18HEDI wall mini-splits; Kinghome KM09HT1DI, KM12HT1DI, KM18HT1DI, KM24HT1DI wall mini-splits; Kinghome KM09HF1DI to KM24HF1DI wall mini-splits (Gree GFH..DA/DB); Kinghome Ultranixx Eco KD24UHO to KD60UHO outdoor units with KD..UHI air handlers; Kinghome Ultranixx cold-climate KU36UHO and KU60UHO outdoor units with KU..UH2I and KD..UHI air handlers

Likely causes

  • Loose sensor plug or poor terminal contact
  • Failed (open or shorted) sensor
  • Fault in the board's sensing circuit

Test and repair steps

  1. Check that the coil/condenser sensor plug is seated fully on the board header.
  2. Unplug the sensor and measure its resistance; compare it with the temperature/resistance chart in the manual appendix.
  3. Replace the sensor if the reading is open, shorted or far from the chart.
  4. If the sensor is good and the plug is secure, replace the control board.

Models that show this code

30 models in Kinghome KM HEDI, Kinghome KM HT1DI, Kinghome KM HF1DI, Kinghome Ultranixx Eco, Kinghome Ultranixx

KD24UHIKD24UHOKD30UHIKD30UHOKD36UHIKD36UHOKD42UHIKD42UHOKD48UHIKD48UHOKD60UHIKD60UHOKM09HEDIKM09HF1DIKM09HT1DIKM12HEDIKM12HF1DIKM12HT1DIKM18HEDIKM18HF1DIKM18HT1DIKM21HF1DIKM24HF1DIKM24HT1DIKU24UH2IKU36UH2IKU36UHOKU48UH2IKU60UH2IKU60UHO

Other codes on the same units

  • E8 High temperature resistance (overload) protection
  • E9 Water overflow protection
  • F0 Refrigerant recovery mode
  • F1 Indoor room temperature sensor fault
  • F3 Outdoor ambient temperature sensor fault
  • F5 Outdoor discharge temperature sensor fault
  • F6 Frequency limit for overload / ODU tube sensor fault
  • F9 Frequency reduced - high discharge temperature

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Kinghome KM09-12-18HEDI service manual, sec. 9.3 status table and 9.4 troubleshooting; Kinghome KM09-12-18-24HT1DI service manual, sec. 9.1 error code list; Kinghome KM09-24HF1DI service manual, sec. 11.1 error code list; Kinghome Ultranixx Eco KD24-60UHO service manual, sec. 3.3-3.4; Kinghome Ultranixx cold-climate KU36/60UHO service manual GC202306, sec. 3.3-3.4. Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.