Bosch · Heat pump

F4 Pressure transducer fault

Medium severity Bosch IDS Light

What the control is telling you

The pressure transducer is not reading correctly.

Applies to: Bosch IDS Light BOVA15 (24/36/60) R-454B heat pump outdoor units

Likely causes

  • Loose CN16 connection
  • Damaged transducer
  • Control board

Test and repair steps

  1. Check the connection at CN16.
  2. Replace the pressure transducer; replace the board if needed.

Models that show this code

3 models in Bosch IDS Light

BOVA15-24BOVA15-36BOVA15-60

Other codes on the same units

  • E52 DC bus voltage out of range
  • E81 EEV coil fault
  • F1 High pressure switch protection
  • F2 System lockout (5 low-pressure trips in 100 minutes)
  • F41 High pressure sensor fault
  • F42 Low pressure sensor fault
  • H01 Drive chip communication fault
  • LED1 green Green LED1 on - main board powered

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Bosch IDS Light installation BTC 762003308 D (02.2025), Fault Code Table 23 and 17.12 Error Code Troubleshooting, p.42-59. Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.