F9 Drive (MOC) internal fault

High severity Trane 5TWR7

What the control is telling you

Internal fault in the drive board. Manual lists only the meaning (A1000BA board); steps are general checks drawn from other sections of the guide.

Applies to: Trane 5TWR7 multi-speed heat pump (5TWR7024A-060A)

Likely causes

  • Loose AOC-MOC harness
  • Drive or control board fault

Test and repair steps

  1. Warning: After power off, wait 2 minutes - the inverter can hold 400 VDC. Confirm under 42 VDC at the +DC/-DC test points before touching the board.
  2. Check the AOC-MOC interface harness between the control and the drive.
  3. Cycle power and watch whether the fault returns.
  4. Replace the drive or control board if wiring is good.

Settings for these units

Outdoor unit placement · Trane 5TWR7

ItemValue
Above unit5 ft clear
Service side3 ft
Walls / shrubs12 in. min
Pad1 in. larger than unit all round, level, separate from house
Cold climate (HP)raise 3-12 in. above pad
Within 1 mile of salt wateradd BAYSEAC001 if no factory salt shield
Operating rangecooling 55-120 F, heating 0-66 F

Avoid bedroom walls and under roof drip lines.

Dimensions and weights · Trane 5TWR7

ModelH x D x W (in.)Weight (lb)
5TWR7024A41 x 30 x 33181
5TWR7036A41 x 30 x 33194
5TWR7048A41 x 34 x 37231
5TWR7060A41 x 34 x 37241
5TTR7024A41 x 30 x 33176
5TTR7036A41 x 30 x 33189
5TTR7048A41 x 34 x 37226
5TTR7060A41 x 34 x 37236

Weights are estimated, uncrated.

Models that show this code

4 models in Trane 5TWR7

5TWR7024A5TWR7036A5TWR7048A5TWR7060A

Other codes on the same units

  • F5 AC over-current fault
  • F6 Drive high temperature fault
  • F7 AC input voltage low
  • F8 DC output voltage fault
  • H5 Hard lock: drive AC input over-current
  • H6 Hard lock: high drive IPM temperature
  • H7 Hard lock: high drive PFC temperature
  • H8 Hard lock: high coil temperature

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Trane ODR-SVN002E-EN (5TTR7/5TWR7 installer's guide) - section Integrated Variable Speed Control Board LED Indicators, Table 18 (A1000BA models). Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.