Trane · Heat pump
F5 AC over-current fault
What the control is telling you
Input over-current (software or hardware), PFC IGBT over-current or DC bus hardware over-voltage. Manual lists only the meaning (A1000BA board); steps are general checks drawn from other sections of the guide.
Applies to: Trane 5TWR7 multi-speed heat pump (5TWR7024A-060A)
Likely causes
- Supply voltage out of range
- Voltage drop from loose or undersized wiring
- Drive fault
Test and repair steps
- Warning: After power off, wait 2 minutes - the inverter can hold 400 VDC. Confirm under 42 VDC at the +DC/-DC test points before touching the board.
- Measure incoming line voltage under load; compare with the nameplate range.
- Check the disconnect, breaker and wire size for voltage drop.
- Tighten all line connections at the drive.
Settings for these units
Outdoor unit placement · Trane 5TWR7
| Item | Value |
|---|---|
| Above unit | 5 ft clear |
| Service side | 3 ft |
| Walls / shrubs | 12 in. min |
| Pad | 1 in. larger than unit all round, level, separate from house |
| Cold climate (HP) | raise 3-12 in. above pad |
| Within 1 mile of salt water | add BAYSEAC001 if no factory salt shield |
| Operating range | cooling 55-120 F, heating 0-66 F |
Avoid bedroom walls and under roof drip lines.
Dimensions and weights · Trane 5TWR7
| Model | H x D x W (in.) | Weight (lb) |
|---|---|---|
| 5TWR7024A | 41 x 30 x 33 | 181 |
| 5TWR7036A | 41 x 30 x 33 | 194 |
| 5TWR7048A | 41 x 34 x 37 | 231 |
| 5TWR7060A | 41 x 34 x 37 | 241 |
| 5TTR7024A | 41 x 30 x 33 | 176 |
| 5TTR7036A | 41 x 30 x 33 | 189 |
| 5TTR7048A | 41 x 34 x 37 | 226 |
| 5TTR7060A | 41 x 34 x 37 | 236 |
Weights are estimated, uncrated.
Models that show this code
4 models in Trane 5TWR7
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: Trane ODR-SVN002E-EN (5TTR7/5TWR7 installer's guide) - section Integrated Variable Speed Control Board LED Indicators, Table 18 (A1000BA models). Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.