Trane · Air conditioner

F1 Compressor start-up fault

High severity Trane 5TTR7

What the control is telling you

Compressor failed to start properly. Manual lists only the meaning (A1000BA board); steps are general checks drawn from other sections of the guide.

Applies to: Trane 5TTR7 multi-speed AC (5TTR7024A-060A)

Likely causes

  • Low or high supply voltage
  • Loose compressor wiring
  • Charge problem or closed service valve
  • Dirty coil / poor airflow
  • Compressor or drive fault

Test and repair steps

  1. Warning: After power off, wait 2 minutes - the inverter can hold 400 VDC. Confirm under 42 VDC at the +DC/-DC test points before touching the board.
  2. Confirm supply voltage at the unit matches the nameplate.
  3. Check compressor wiring and terminals at the drive for looseness or burn marks.
  4. Verify refrigerant charge by subcooling and that both service valves are fully open.
  5. Check outdoor coil is clean and airflow unrestricted.
  6. If it repeats with good voltage and charge, check compressor windings and the drive.

Settings for these units

Outdoor unit placement · Trane 5TTR7

ItemValue
Above unit5 ft clear
Service side3 ft
Walls / shrubs12 in. min
Pad1 in. larger than unit all round, level, separate from house
Cold climate (HP)raise 3-12 in. above pad
Within 1 mile of salt wateradd BAYSEAC001 if no factory salt shield
Operating rangecooling 55-120 F, heating 0-66 F

Avoid bedroom walls and under roof drip lines.

Dimensions and weights · Trane 5TTR7

ModelH x D x W (in.)Weight (lb)
5TWR7024A41 x 30 x 33181
5TWR7036A41 x 30 x 33194
5TWR7048A41 x 34 x 37231
5TWR7060A41 x 34 x 37241
5TTR7024A41 x 30 x 33176
5TTR7036A41 x 30 x 33189
5TTR7048A41 x 34 x 37226
5TTR7060A41 x 34 x 37236

Weights are estimated, uncrated.

Models that show this code

4 models in Trane 5TTR7

5TTR7024A5TTR7036A5TTR7048A5TTR7060A

Other codes on the same units

  • E0 Personality module error
  • E1 Configuration error
  • E2 AOC software / configuration mismatch
  • F0 AOC-MOC communication fault
  • F2 Compressor over-current
  • F3 Compressor control fault
  • F4 Outdoor fan control fault
  • F5 AC over-current fault

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Trane ODR-SVN002E-EN (5TTR7/5TWR7 installer's guide) - section Integrated Variable Speed Control Board LED Indicators, Table 18 (A1000BA models). Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.