Viessmann · Mini-split
F0 Current overload protection
What the control is telling you
Same fault as PC08. Shown on the 48K high heat model.
Applies to: DLCMHBH48EAK (48K high heat) only
Test and repair steps
- Safety kill power at the disconnect and wait for the inverter capacitors to discharge before touching boards or wiring.
- Measure the input current on the supply wire. Limits: 15 A on 18K; 18.5 A on 27K and 18K high heat; 22.5 A on 36K and 27K high heat; 28 A on 48K and 36K high heat.
- Outdoor air above 122 F (50 C) = outside the range, shut it down.
- Check outdoor airflow and clean the coil.
- Check for a refrigerant restriction. If blocked: recover the charge, blow the lines through with nitrogen, evacuate and recharge.
- If none of the above, replace the outdoor main board (or the electric control box) and retest.
Models that show this code
7 models in Viessmann Vitocal 200-S DLCM(R/H)B multi-zone outdoor
Other codes on the same units
Save it for the next call
Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.
Source: DLCMRBH/DLCMHBH Multi-Zone Outdoor Service Manual (sold as Midea, Carrier and Viessmann Vitocal 200-S; Viessmann doc 6225551-03, 12/2024), Table 24 Outdoor Unit Error Display (48 High Heat only) p.27; diagnosis p.64-65. Summarized in our own words; check the original manual for your model.
Homeowner looking at this code? See what it means for you and when to call a technician.
For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.